So our power bills have been higher than expected. We had our HVAC person in yesterday to try and fix a problem with some windows (on motors) that won't stay open, and one thing we looked at was recirculating hot water, or hot water on demand. I asked the engineer about it when the plumber and contractor suggested it, and he thought that with the water going through insulated joists, that there shouldn't be much concern. The photo is of a few day history of the DHW (top and bottom of the tank), and the GSHP (ground source heat pump), with both the load and source shown. The GSHP has been kicking in when we take a shower, but this heats the water to about 100-110, the last bit is topped off by a coil in the tank. Towards the end of yesterday you can see where we turned off the recirculating pump. The gist is that we have been spending not only a lot of energy on the system to keep hot water always available at any sink or shower, but also, it has been re-heated exclusively by the coil. Which is a double whammy, because the coil is 100% efficient, but the GSHP is running at about 450% efficiency. Since we are quite early in our power bill cycle, we should see a big dip in the next bill.