I don't want to hijack the thread, but along the lines of the title of the OP, "Meter and test every show"...
Here's my story from a few weeks ago:
We show up at a commercial building set up as a senior center of sorts, but with a big hall for the concert. The building is pretty old and has several electrical closets with step-down transformers (480V to 208V), and I found a panel with some space to power up my rig. I checked the entire panel leg to leg and leg to neutral and leg to ground before I started, and the results were interesting. All hots metered to the other hots were 240V, which is very unusual on a 3-phase service, as they are normally 208V. Metering hots to neutral I got about 120, 120, and 208. If you know anything about power, you immediately know that it is a wild-leg 3-phase delta service with one transformer center-tapped to provide the neutral for two immediately adjacent hot legs. This is totally fine - not a problem as long as you only use the two 120V legs. So I proceed to tie in and everything meters great.
Next I start plugging in things and after plugging in a rack with a Furman I hear a big POP. The rack isn't on. I check the power LEDs on a few different pieces of gear and find that my subs are going crazy turning on and off. I meter again and find the voltage fluctuating wildly between about 8 and 200 volts.
The problem? Bad neutral somewhere. Not in my rig anywhere, but somewhere between the transformers and the panel I was using. The power would meter fine until I connected a load of even a 150W LED par can, when it would fall apart.
We couldn't use the power and I didn't feel like trying the other electrical closet, so we used wall power.
The only piece of gear lost was the Furman, where the MOVs failed shorted hot to ground.