In light of the persistently short-sided policies regarding linking exhibited on PSW that resulted in others' posts being removed, I voluntarily removed a post today and transitioned it here. Hopefully it is helpful for those looking to learn some of the vocabulary from the NEC:
The code cycle I reference is the 2011 NEC, while being mindful of the upcoming 2014 cycle based on the 2013 code draft. In many cases I'm paraphrasing the code definitions and statements, please see the NEC for the full definition. If I quote the code directly, I'll indicate that by placing "quotes" around the text. Code quotes with brackets [ROP x-x] after them refer to quotes from the code in sections where I am quoting proposed changes for the 2014 code cycle. The proposed changes have improved definition clarity, and are worth mentioning.
This first post is definitions. All definitions for the NEC are in article 100 (NEC 100). These are selected set of definitions relevant to the code terminology that discusses generators and their grounding. These definitions are listed in numerical order such that they build on each other. Once it is clear that people grasp the definitions, we can move on to generators and grounding using the vocabulary of the code. Mike might end up splitting this out into a separate thread:
Terminology Definitions (NEC 100)
Bonding - "Connected to establish electrical continuity and conductivity." Connection of two electrically conducting elements together achieves two main purposes:
Grounding - Physically connecting an electrical system to the contents of planet earth.
Grounding Electrode - the physical conductor that ties to planet earth to facilitate grounding
Grounded - An electrical conductor physically connected to the earth by nature of it being bonded to a grounding electrode or grounding electrode system
Grounding Electrode Conductor (GEC) - A conducting element used to connect a grounded conductor to a grounding electrode
Bonding Jumper - "A reliable conductor to ensure the required electrical conductivity between metal parts required to be electrically connected."
Ground Fault - "An unintentional, electrically conductive connection between an ungrounded conductor of an electrical circuit and the normally non–current-carrying conductors, metallic enclosures, metallic raceways, metallic equipment, or earth. [ROP 5–11]"
Equipment Grounding Conductors (EGC) - The conductive path(s) that provides a ground-fault current path and connects normally non–current-carrying metal parts of equipment together and to the system grounded conductor or to the grounding electrode conductor, or both. [ROP 5–14a]
Service - "The conductors and equipment for delivering electric energy from the serving utility to the wiring system of the premises served."
Separately Derived System - "A premises wiring system or portion of a premises wiring system other than a service. Power for such systems is derived from a source of electric energy or equipment with no direct connection from circuit conductors of one system to circuit conductors of another system, other than connections through the earth, grounding electrode(s), grounding electrode conductors, bonding jumpers used to connect grounding electrodes, equipment grounding conductors, metal enclosures, or metallic raceways. [ROP 5–20]"
Overcurrent Protective Device (OCPD) - A device that opens a circuit if the current rises above a certain amount. Think a circuit breaker or fuse.
Effective Ground-Fault Current Path - "An intentionally constructed, low-impedance electrically conductive path designed and intended to carry current under ground-fault conditions from the point of a ground fault on a wiring system to the electrical supply source and that facilitates the operation of the overcurrent protective device or ground-fault detectors. [ROP 5–6]"
Note that NEC, especially in older editions, plays overly loose with grounding or grounded where often the author meant to refer to bonding. The new, upcoming code cycle for 2014 is more consistent in its wording, but grounding terminology can still be found in circumstances that actually discussing bonding.
The code, and your local authority having jurisdiction (AHJ) are the ultimate authorities on electrical matters.
- A) It holds the points at the same voltage potential
- B) Serves as a path for current in the event that a voltage potential difference (e.g. from an external voltage source) creates a current flow.
- Informational Note No. 1: It is recognized that the equipment grounding conductor also performs bonding.
- Informational Note No. 2: See 250.118 for a list of acceptable equipment grounding conductors."