I don't know of any exception in the NEC, but I doubt most local inspectors would mind the appropriate use of cable tray in this application.  It's better than the alternatives.


Article 392 covers cable tray, and all it has to say about non-horizontal runs is to securely fasten the cables to transverse members of the cable tray.  That may be difficult with a 15' vertical run (how are you planning on running those cables?).