Hi gentlemen
I have 4 ..30 amp small packs that I need to be able to use at 2 different setups. .
I need to find a cheap (lol) distributor for some soow 6/4 and make 2 different 50amp distro to 2 30 amp small packs
the small packs are 24 amp each so 48 in total
is this possible. .
I'm in Canada so not sure if professional homage ones are Ok. ...
thanks
 
24A load per 30A unit as in 80% of the 30A maximum rating? If that's the case, a 50A feed is too small for both, unless you manage to find equipment and branch circuit breakers rated for continuous operation at full load. There are some exceptions for certain load types, though. What's connected to this distro?
 
20170226_161054.jpg Typical 3 way system and monitors/lights
​​​​​powersoft K10...4x (2×18)..subs
K3..4x15/2"..mids/high
2x K3. .monitors
6-10 LED lights