Re: L14-30 ConnectorsThere are really no motors that take an L14-30, unless it's a single phase 240V motor and you're not using the neutral, or it's a single phase 120V motor and you're not using one hot.Proper connector for 3 pole/4 wire 3 phase operation is the L15 series:http://www.grainger.com/Grainger/LEVITON-Locking-Plug-1PKK5And I'm also not aware of any motors that require anywhere close to 30 amps.Since I know that you know what you're doing with power, I should ask, what's the bigger picture here?
Re: L14-30 Connectors
There are really no motors that take an L14-30, unless it's a single phase 240V motor and you're not using the neutral, or it's a single phase 120V motor and you're not using one hot.
Proper connector for 3 pole/4 wire 3 phase operation is the L15 series:
http://www.grainger.com/Grainger/LEVITON-Locking-Plug-1PKK5
And I'm also not aware of any motors that require anywhere close to 30 amps.
Since I know that you know what you're doing with power, I should ask, what's the bigger picture here?